Switch Problems

Posted: Thu Sep 22, 2011 8:39 pm
by keithe
Hi
I am using Winlog Lite to communicate with an ADAM 6051
It communicates OK using Modbus RTU TCP with an IP address of 192.168.0.81
I can read the inputs perfectly, but when it comes to setting one of the outputs ON using the Toggleswitch gadget, nothing happens.
If I set said output ON, via other means, the Toggleswitch gadget detects this and changes from OFF to ON as expected.
However, clicking on the Toggleswitch gadget has no effect.
Please help, I am tearing my hair out here.
Regards
Keith

Re: Switch Problems

Posted: Fri Sep 23, 2011 10:53 am
by admin
Hi,
is "Need apply" property set "No"?

Re: Switch Problems

Posted: Fri Sep 23, 2011 2:14 pm
by keithe
Hi,
Thank's for replying.
I have tried setting the NEED APPLY property to both YES and to NO. it doesn't help.
Which setting is correct, I find the help is a little unclear on this

Re: Switch Problems

Posted: Fri Sep 23, 2011 8:10 pm
by keithe
Hi
I have fixed it now.
There were multiple problems:
I had the gate configured wrongly, plus a problem with user access levels and also, "Need Apply was set to YES.
In addition, I have found, that, when using WinLog that the modbus addresses are out by one.
To control DO0 I must write to 0x16 instead of 0x17 as stated in their docs, for instance. I am thinking that it may be based at zero instead of one, as all the addresses are like this.

Thanks for your help
Keith