Hi, i have this question..on a PC i have my XWAY driver installed, with my XIP configuration for ethernet connection with Telemecanique TSX that is working good. I have decide to change the actual scada (Monitor Pro by Schneider) and i want to use Winlog. I don't want to change nothing on the PLC, so i need to know if it's possible to work with this kind of driver with winlog.
Thanks
Lorenzo
Telemecanique TSX ethernet connection by XWAY driver
-
- Posts: 19
- Joined: Tue May 17, 2011 11:02 am
Re: Telemecanique TSX ethernet connection by XWAY driver
Dear Sir,
XWAY is a proprietary protocol not supported by Winlog.But normally plc also support the Modbus TCP protocol, check if your plc is compatible with the modbuss RTU TCP.
Best Regards
XWAY is a proprietary protocol not supported by Winlog.But normally plc also support the Modbus TCP protocol, check if your plc is compatible with the modbuss RTU TCP.
Best Regards
-
- Posts: 19
- Joined: Tue May 17, 2011 11:02 am
Re: Telemecanique TSX ethernet connection by XWAY driver
Thank you so much, Modbus RTU TCP is working good!!! Very simple and fast to setup.