Re: ModbusTCP

Post by admin »

Dear Sir,
normally 400001 address is in "holding register" table. For reading holding register you must use the function "3" (see help) in Winlog; then in Gate Builder you have to insert address 3:0001 or 3:0000 (depending on your device's mapping, try both).
Can I leave a template open in Runtime and go into Project Manager to make changes?
Will the changes show without restarting Runtime?
No, for gate and protocol you have to restart Runtime.

If it doesn't work please send you test application, we check it.